WCP3700 not delivering full power

I installed a WCP3700 at the start of the year to control a 3kW Titanium element in my hot water cylinder. The element and cylinder are 5 years old.

This has been working fine until about the last month when I noticed the heating seems very slow.   Today I fitted a current clamp to the wire in my switch board, even at 100% power it is only showing around 7A when the element should draw 15A.

I need to investigate why it is not heating at the required speed. 

Could the PWM pulses damage the element ?

I have rebooted the WCP3700.

There is a second element fitted lower in the cylinder with a direct relay connection - this draws 15A.


I'm looking at the simplest way to test:

- I will bypass the controller next week when I get time to see if it is the WCP3700 but this requires a long length of wire.

- I could swap the elements over but then I need to drain the cylinder.


Any other suggestions are welcome


NB: I have 5 DS1820 temperature sensors fitted to the cylinder so can measure the rate of temperature rise easily.

Thread Status
14
411
2
1
0

Sort replies by:

Hi, 

Hi,what you used in an pure resistive electrical heater ,not a heat pump, yes?
The life of the pure resistive heater would not be affected by the PWM voltage.

Please check whether the max power is set correctly ,only when the set power is equal to the max power , it will reach the 100% power output

https://www.iammeter.com/quickstart/wpc3700-quickstart#4-parameter-settings


Yes it is a 100% resistive element (not a heat pump)

I have configured the max power to 3000W.

I will do some other tests this week.

Please use this api and check whether the maxpower and setpoewr are the same in return.

https://www.iammeter.com/newsshow/api-wpc3700#apigetadv


Here's the output of running the API


{"setPowerMode":0,"meterConfig":"3,2,1","threshold":0,"hysteresis":0,"tzOffset":12,"startHour":4,"stopHour":19,"meterType":0,"restorePower":125,"ntpServer":"ntp1.aliyun.com","haDiscovery":0,"mqttEnabled":0,"mqttAddress":"","mqttUsername":"","mqttPassword":"","meterList":"iMeter,virtualTCP","setPowerModeList":"Manual,Auto","maxPower":3000,"setPower":3000,"meterAddress":"192.168.0.20","uploadInterval":60}


I have been monitoring power consumption using my WEM3080T-150 and it seems the wpc is only delivering 50% of the power. I'm guessing it has a pair of triacs ? in which case has one failed ?

My colleague replied to me as below
If the triacs fail, it would output 100% percent,n ot 50%。
If possible, please measure the voltage output by a multimeter(Please take care in operation). if it output 220V (full range of the grid voltage), it means the WPC3700 works correctly.

At set power 1,000W volts are 86

At set power 2,000W volts are 15

At set power 3,000W volts are 128


The unit is set to max power = 3,000W. The 3 phase WEM3080T-150 meter is about 50m away and shows approx 240v for this phase.

So it appears to be outputting around 1/2 the max power. This only happened about a month ago.

That second reading was "115" volts

At set power 1,000W volts are 86At set power 2,000W volts are 15At set power 3,000W volts are 128The unit is set to max power = 3,000W. The 3 phase WEM3080T-150 meter is about 50m away and shows approx 240v for this phase.So it appears to be outputting around 1/2 the max power. This only happened about a month ago.

Hi,

Please confirm 

At set power 1,000W volts are 86

At set power 2,000W volts are 150   yes?

At set power 3,000W volts are 128


Do you mean the voltage is 150v in power of 2000w but  drop to 128v when the power is set to 3000w, yes?


Please use this API 

HTTP://{local ip}/api/monitor 

and provide the return json value when the set power is 

2000w  

2200w

2400w

2600w

2800w

3000w.

Focus on the voltageAD and voltageADSet but we also need to whole return JSON value.

Please help me to provide the API return, and then I think maybe we will be sure what happened.


This only happened about a month ago.

I note this before, but as I said before, if the triacs fails ,the voltage would pass totally ,not only a part ,so we are also curious about this issue.



Sorry, for 2000W it was 115V.
I will send the json values in the next post


For 2,000W

{"ssid":"xx","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":2664,"voltageAdSet":2664,"gridPower":0,"maxPower":3000,"setPower":2000,"model":"WPC3700","temperature":28,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}

For 2200W

{"ssid":"xx","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":2889,"voltageAdSet":2889,"gridPower":0,"maxPower":3000,"setPower":2200,"model":"WPC3700","temperature":30,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}

For 2400W

{"ssid":"xx","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":3148,"voltageAdSet":3148,"gridPower":0,"maxPower":3000,"setPower":2400,"model":"WPC3700","temperature":30,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}

For 2600W

{"ssid":"x","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":3448,"voltageAdSet":3448,"gridPower":0,"maxPower":3000,"setPower":2600,"model":"WPC3700","temperature":30,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}

For 2800W

{"ssid":"xx","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":3796,"voltageAdSet":3796,"gridPower":0,"maxPower":3000,"setPower":2800,"model":"WPC3700","temperature":31,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}

For 3000W

{"ssid":"xx","sig":57,"mac":"849DC27FEB75","version":"i.76.058.8","method":"286-2054","server":"em","SN":"C355X8HVG4","voltageAD":4096,"voltageAdSet":4096,"gridPower":0,"maxPower":3000,"setPower":3000,"model":"WPC3700","temperature":31,"driver":2054,"restorePower":125,"setPowerMode":0,"meterAddress":"192.168.0.20","meterOnline":0,"threshold":0,"hysteresis":0,"startHour":4,"stopHour":19,"currentHour":21,"tzOffset":12,"meterType":0,"meterConfig":"3,2,1","meterList":"iMeter,virtualTCP","ntpServer":"ntp1.aliyun.com","setPowerModeList":"Manual,Auto"}


Thanks for your sharing .

The "voltageAD" and "voltageAdSet" values are both correct.

Could you mind also let me know whether the real voltage output on these powerset values?



As requested

2000w  113V

2200w 118V

2400w 124V

2600w 127V

2800w 127V

3000w 125V

The line voltage is nominal 230V (+/- 6%)

It seems that the device has developed a fault.
We are very sorry for this inconvenience.

Please email us ([email protected]) with your address and phone number.
We will arrange a replacement to be shipped from Germany tomorrow.

To express our apologies, we would like to offer you 5,000 reward points.
You can request them here:
How to earn rewards points with IAMMETER

In addition, after removing the old unit from your installation, if possible, please help us by removing its shell and taking some clear photos of the PCB.
Kindly send these photos to us by email as well — we would like to analyze them to better understand the cause of the fault.

We sincerely apologize again for the trouble and greatly appreciate your assistance.

No problems - I have sent my address via email. I will dismantle and photograph the existing unit when it has been replaced