hi
how can i connect a 3 phase battery system with 3 seperate 2kw on grid inverters
i have installed :
1x 3080T to monitor the gird L1 L2 L3 in/out
1x 3080 to monitor one PV on grid inverter L1
1x 3080T to monitor two PV on grid inverter L2 and L3
two seperate DC PV Charger feed in to the battery
i will monitor the 3 seperate on grid Inverters from DC to AC
can i use one 3080T and configure the Type as "AC-Storage" ?
an then all OUT power from the battery will monitored ?
br Harry
1x 3080T to monitor the gird L1 L2 L3 in/out
OK
1x 3080 to monitor one PV on grid inverter L1
1x 3080T to monitor two PV on grid inverter L2 and L3
OK, but if the inverter of L1 and inverter of L2 and L3 are installed close, you can consider using one WEM3080T to monitor them together.
two seperate DC PV Charger feed in to the battery
i will monitor the 3 seperate on grid Inverters from DC to AC
Sorry ,the WEM3080 and WEM3080T can only be used to measure the AC parameter, not the DC parameter.
So you can only install it to the position of AC output(inverter output),not the position of DC output(solar pannel or Battery)
can i use one 3080T and configure the Type as "AC-Storage" ?
The "ac storage" is an integration of DC battery and inverter.
It can charge by an AC grid system and discharge to the AC grid system.
IAMMETER has the "meter type" of "ac storage" because it will calculate the energy flow in the system.
an then all OUT power from the battery will monitored ?
So you can only install it to the position of AC output(inverter output),not the position of DC output(solar pannel or Battery)
yes that is what i mean π
Hi,
Sorry, if there is still a question,
please give us a simple sketch map to illustrate how do you want to install the energy meter, I still have not understood the question now.