Double CT calculation problem differrent result on IAMMETER Docker local version
I found problem about Double CT calculation, select the same ct ratio and a same iMeter device but result bad differrent,
IAMMETER Cloud version (iammeter web) setting CT ratio:
IAMMETER Docker version (local install) setting CT ratio:
IAMMETER Cloud version (iammeter web) calculation result:
IAMMETER Docker version (local install) calculation result:
Hi,
Your feedback has been received, we will reply to you as soon as possible.
And reminding you that it is best to pixelate your SN in your picture.
BR
https://hub.docker.com/r/iammeter/iammeter
docker image iammeter/iammeter:1.6(or iammeter/iammeter:latest) Fixed the CT ratio bug.
now you can use this one.
👍👍👍
the product do not support this CT(150A:75ma) in double CT solution.
If you want to use double ct, only xxx:5A ct can be used in primary CT.
Wie kann ich CT auf 150A / 75mA einstellen?